Can you please let me know the Exhaust flow rates to be considered for UPS AND BATTERY ROOM EXHAUST AND MENTION STANDARD REFERENCE
Hi, do you know any factory that can supply ducting (not form or form up are ok) to Singapore from JB? We are ducting installer in singapore.
Hi Yu,
Can you Please share the Data center Cooling Load CALCULATION spread sheets and Standards , if available?
Hi, have a question here... I have designed a staircase Pressurization system to keep the 50Pa pressure Difference...i have considered VFD System Differential pressure system within the staircase at lower and higher levels...Do i need to consider the Relief Damper? if yes, can i delete the VFD and run constant speed Fan?..which is more reliable? Pls suggest
If reliability is more important I would go with a simple system. Engineering principle is: fewer parts = more stability. No sensors no VFD less things that can break or fail. Just a constant-speed fan and properly sized relief damper (set not to exceed 60 Pa).
Hi Kiran,
In extent to the above sharing, I would add that all FCUs should be tested to their design flow rate. If all FCUs are ON at the same time, you may not get full flow due to diversity design. Hence, group them as per your design basis for diversity and test them in groups. That way, you ensure all FCUs can meet their designed flow and the chillers can be tested to full load.
Thanks.
I have a customer with a lab environment building. They have a 10x15 storage room storing sensitive chemicals that needs to be cooled to 60 degrees year round but they do not want a gas refrigerant used for the evaporator fan coil. My question is how to find a small enough water chiller for a room this size? I would appreciate your thoughts, Thanks!
They do not have a chiller on the building. Do you offer design help if the customer wants to go with the custom option? I could do a block load calc on the room
Sorry for the late reply but yes, I do help with design.
Hi, I have a question, in one of my recent projects, I proposed relief cooling for the toilets , without any dedicated fan coil units for the toilet.relief air is recircilated fresh Air from the Energy recovery unit...can you pls confirm, if this approach also works?
It works as long as you have adequate air change in the toilet.
Hi, is a dedicated fan coil unit is required for the store room..within the conditioned office space?
Depending on the store room temp requirement, usually a basic exhaust fan will do as it pulls cold air from the adjacent room for mild cooling and meet basic ventilation needs.
In case of Trane Centrifugal Water Cooled Chiller of 650 TR (Primary Constant, Secondary Variable), will there be any saving from putting VFD in modulation on Cooling Tower Fan or Condenser Pump. Or will that be counter productive. What best logic to deploy to mange the trade -off. Please advise
Makes sense, thank you Yu Chang...please advise on the suitable logic for VFD Modulation for Cooling Tower
Hi YU,
Please find attached the image and provide the clarification about ventilation of Barbeque and hot pot table in House.i Highlighted the Grille location.Looking for your reply
how to meet the 20%RH humidity